On 4/14/21 5:40 PM, Carlos E. R. wrote:
Hi,
I have one UPS (with an almost dead battery) and I want to at least see it with NUT. When I connect it, I see in the log:
You need to set a few setting in the /etc/ups files. Here is how I have a ups setup with nut on host valkyrie that has a ups I name "valkyrie_ups" for nut. Only the uncommented lines are shown under the config file name and the password is needed where I have "MyPassword": (the noc script below is just my "no comment" script that picks out lines not commented using sed) $ for i in *.conf; do printf "\n%s\n\n" $i; noc $i; done hosts.conf MONITOR valkyrie_ups@localhost "Valkyrie CP1350PFCLCD UPS" nut.conf MODE=standalone ups.conf [valkyrie_ups] driver = usbhid-ups port = /dev/hiddev0 desc = "Valkyrie CP1350PFCLCD UPS" upsd.conf upsmon.conf MONITOR valkyrie_ups@localhost 1 david MyPassword master MINSUPPLIES 1 SHUTDOWNCMD "/usr/bin/systemctl poweroff" POLLFREQ 5 POLLFREQALERT 5 HOSTSYNC 15 DEADTIME 15 POWERDOWNFLAG /etc/ups/killpower RBWARNTIME 86400 NOCOMMWARNTIME 300 FINALDELAY 5 upssched.conf CMDSCRIPT /usr/bin/upssched-cmd upsset.conf I_HAVE_SECURED_MY_CGI_DIRECTORY -- David C. Rankin, J.D.,P.E.